Fire ratings for partitions between tenant spaces in a multi-tenant building are governed by the International Building Code (IBC), which the NCIDQ IDPX exam references for code compliance. The specific requirement depends on the occupancy types, the presence of a sprinkler system, and the number of occupants.
Occupancy Classification:A bank typically falls under Business (B) occupancy, while a restaurant serving more than 49 persons is classified as Assembly (A-2) occupancy. The adjacent insurance office is also a Business (B) occupancy.
Fire Separation Requirement:According to the IBC, in a non-sprinklered building, a change in occupancy from Business to Assembly requires a fire-rated separation between the new Assembly space and adjacent tenant spaces. Table 508.4 of the IBC specifies that a 1-hour fire-rated separation is required between A-2 (Assembly) and B (Business) occupancies when the building is not sprinklered.
Impact of Sprinkler System:The question specifies that the building is non-sprinklered. If the building were sprinklered, the fire rating might be reduced or eliminated, depending on the code allowances, but in this case, the 1-hour rating applies.
Number of Occupants:The restaurant serving more than 49 persons confirms its A-2 classification, as Assembly occupancies are defined by occupant loads greater than 49. This does not change the fire rating requirement but confirms the occupancy type.
Option A (0):A 0-hour rating would not comply with the IBC requirement for separation between A-2 and B occupancies in a non-sprinklered building.
Option B (1):A 1-hour fire-rated separation is the minimum required by the IBC for this scenario, making this the correct answer.
Option C (2):A 2-hour rating is not required unless the occupancies involved have a higher hazard classification (e.g., hazardous materials) or the building has specific structural requirements, which is not indicated here.
Option D (3):A 3-hour rating is typically reserved for more hazardous occupancies or fire walls, not for tenant separations in this context.
Verified Answer from Official Source:
The correct answer is verified from the International Building Code (IBC), as referenced in NCIDQ IDPX study materials.
“Table 508.4 – Required Separation of Occupancies (hours): A-2 (Assembly) and B (Business) – 1 hour (non-sprinklered).” (International Building Code, 2018 Edition, Table 508.4)
The NCIDQ IDPX exam tests knowledge of building codes, specifically the IBC, which requires a 1-hour fire-rated separation between A-2 and B occupancies in a non-sprinklered building. This ensures safety by containing potential fire spread between spaces with different occupancy risks.
Objectives:
Apply building codes to determine fire separation requirements (NCIDQ IDPX Objective: Codes and Standards).
Understand occupancy classifications and their impact on fire ratings (NCIDQ IDPX Objective: Building Regulations).
[References:, International Building Code (IBC), 2018 Edition, Table 508.4., NCIDQ IDPX Study Guide, Codes and Standards Section., ]