Do you need to consider blast protection when designing a data center?
You are allowed to use a calculator for this question.
A computer room has a net volume of approximately 2,500 m³ / 88,287 ft³.
The temperature is 20 °C / 68 °F.
The required design concentration is 7%.
The S-Factor is 0.1359 (metric) / 1.885 (imperial).
Calculate the amount of gas required for this computer room based on FM200. What is the correct weight?